We have a project on the go @ Engen Refinery, Durban, South Africa for online piping inspections in accordance with API570. Recently, we incorporated an audit system to verify the acurateness of the UTWT results. The idea behind the audit is not to target the qaulified NDE technicians, but rather to find better ways of repeating TML's (thickness monitoring locations) and surface preparation. Now the big question: What would be a acceptable tolerence on a repeat reading the day later? We all know that it is very difficult (if not impossible) to repeat the exact reading on old piping. Are there a paper available for guidance?
Regards
Poena (HPIA Site Manager)



 
 Reply 
 
Navita
Navita
08:09 Jul-17-2008
Re: Online UTWT acceptable tolerences
Probably Mr. Dinesh Gupta, an ASNT Level-III in 7 methods could help you out. Mr. Gupta is based in India, but travels globally for such problems. You can contact him on guptadinesh1966@yahoo.com

----------- Start Original Message -----------
: We have a project on the go @ Engen Refinery, Durban, South Africa for online piping inspections in accordance with API570. Recently, we incorporated an audit system to verify the acurateness of the UTWT results. The idea behind the audit is not to target the qaulified NDE technicians, but rather to find better ways of repeating TML's (thickness monitoring locations) and surface preparation. Now the big question: What would be a acceptable tolerence on a repeat reading the day later? We all know that it is very difficult (if not impossible) to repeat the exact reading on old piping. Are there a paper available for guidance?
: Regards
: Poena (HPIA Site Manager)
------------ End Original Message ------------




 
 Reply 
 
Rohit Bafna
,
TCR Engineering Services, India, Joined Sep 2007, 18

Rohit Bafna

,
TCR Engineering Services,
India,
Joined Sep 2007
18
00:58 Jul-19-2008
Re: Online UTWT acceptable tolerences
You should look at Credo Soft which has a product for wall thickness measurement and recording. Visit http://www.credosoft.com/download/Wall%20Thickness%20and%20Anomalies.pdf

Look at the Credo PRO software at http://www.credosoft.com/products.htm

Our company, TCR Engineeeing (www.tcreng.com) can help you define an acceptable tolerence guideline based on your corrosion rates and material specifications.

Please note we at TCR work with PP SIMTECH to design and deliver RBI solutions to clients as well.


 
 Reply 
 
Ryan Burns
Ryan Burns
01:59 Jul-19-2008
Re: Online UTWT acceptable tolerences
----------- Start Original Message -----------
: We have a project on the go @ Engen Refinery, Durban, South Africa for online piping inspections in accordance with API570. Recently, we incorporated an audit system to verify the acurateness of the UTWT results. The idea behind the audit is not to target the qaulified NDE technicians, but rather to find better ways of repeating TML's (thickness monitoring locations) and surface preparation. Now the big question: What would be a acceptable tolerence on a repeat reading the day later? We all know that it is very difficult (if not impossible) to repeat the exact reading on old piping. Are there a paper available for guidance?
: Regards
: Poena (HPIA Site Manager)
------------ End Original Message ------------

Hello Poena,

I have never come across a paper on this, but I would be surprised if one did not exist. I believe the most practical approach is the one I was taught years ago by a very smart man and pioneer in corrosion survey development.We were able to go back to a vessel or piping component years later and, in a very low corrosion service, repeat the reading exactly, or +/- 2 mils. Some obvious things to consider are;
1- Use the same instrumentation between all UT data collection crews.
2 - Att techs should use the same exact calbration wedge and always do a two point calibration within the range to be measured.
3 - Use the same make of probe (dual element) with acceptable wear between crews. Use the probe within manufacturers specs, most say aove 120 deg F, a high temp transducer and/or delay line is required.
4 - Mark the TML points with indeliable paint. If you do a minimum scan along, say the extrados of an elbow, mark the exact scan area.
5 - Check the calibration frequently, especially if scanning as opposed to single point readings.
6 - Use a proper couplant, not grease or the like, as each tech will have different transducer application pressure.
7 - Record the temperature of the component at time of inspection. Proceduralize how elevated temp components are handled, either heating cal block, temp compensation, or standard ambiant cal with repeat UT done when vessel is always on or off line with a consistant temperature.

As I write this, I realize I could go on for a while....hope some of this helps, and if you do come across a technical paper on this please let us (the forum) know.

PS - Most sowftware (not just CredoPRO) with upload interfaces have a built in QA function of % to last reading. This is good, but proper procedures and trained techs is paramount.

Regards,

Ryan.


 
 Reply 
 
Arun
Arun
05:52 Jul-20-2008
Re: Online UTWT acceptable tolerences
We can do consultancy for this situation since I worked In brunei Shell facility for 5 years for doing TML UT wall thickness doing corrosion monitoring-Arunachlam.NDT level 3 , contact me at arun@cutechinspection.com-
---------- Start Original Message -----------
: Probably Mr. Dinesh Gupta, an ASNT Level-III in 7 methods could help you out. Mr. Gupta is based in India, but travels globally for such problems. You can contact him on guptadinesh1966@yahoo.com
: : We have a project on the go @ Engen Refinery, Durban, South Africa for online piping inspections in accordance with API570. Recently, we incorporated an audit system to verify the acurateness of the UTWT results. The idea behind the audit is not to target the qaulified NDE technicians, but rather to find better ways of repeating TML's (thickness monitoring locations) and surface preparation. Now the big question: What would be a acceptable tolerence on a repeat reading the day later? We all know that it is very difficult (if not impossible)to repeat the exact reading on old piping. Are there a paper available for guidance?
: : Regards
: : Poena (HPIA Site Manager)
------------ End Original Message ------------




 
 Reply 
 

Product Spotlight

MUSE Mobile Ultrasonic Equipment

The MUSE, a portable ultrasonic imaging system, was developed for in-field inspections of light-weig
...
ht structures. The MUSE consists of a motor-driven manipulator, a water circulation system for the acoustic coupling and a portable ultrasonic flaw detector (USPC 3010). The MUSE provides images of internal defects (A-, B-,C- and D-scan).
>

Aerospace Systems - Automated Ultrasonic Inspection

USL are specialists in the design and manufacture of turnkey ultrasonic inspection systems for aer
...
ospace applications. From monolithic composites to complex honeycomb structures. This video shows just a few examples of what is possible, find out more at: www.ultrasonic-sciences.co.uk
>

High-performance Linear Phased Array Probes

Available to order from stock in a range of 5MHz – 7.5MHz and from 16 to 64 elements. Designed w
...
ith piezo-composite elements, Phoenix phased array probes provide high-resolution imaging to maximise sensitivity; accurate ultrasonic detection and sizing of defects in welds; and effective corrosion mapping. Housed in a rugged stainless steel case for on-site industrial NDT applications.
>

Magnetic X-Ray Pipeline Crawler

Zhong Yi brand pipeline crawler is magnetic/micro-video controlled crawler with DC X ray unit inst
...
alled for checking welding of pipeline. Move steadily inside the pipeline 6''-60''diameter with speed of up to 18m/min, Max. moving diatance 5 kilometers and provide the efficient inspection of the pipeline.
>

Share...
We use technical and analytics cookies to ensure that we will give you the best experience of our website - More Info
Accept
top
this is debug window