where expertise comes together - since 1996 -

The Largest Open Access Portal of Nondestructive Testing (NDT)

Conference Proceedings, Articles, News, Exhibition, Forum, Network and more

where expertise comes together
- since 1996 -

9916 views
Technical Discussions
S.R.G.PRABHU
Consultant, AUT specialist
FREELANCE, India, Joined Aug 2008, 64

S.R.G.PRABHU

Consultant, AUT specialist
FREELANCE,
India,
Joined Aug 2008
64
01:39 Mar-30-2008
API-510 Pressure vessels inspection frequency

Hello,
I am working on a Gas gathering platform offshore. We need to know the frequency of the pressel vessels inspection, internal visual...As per API 510, what is the frequency of a vessel to be inspected which is 2 and half years old?Someone please advise.Is it once in 5 years?We have a shut down coming and planning has to be done.


 
 Reply 
 
Ryan Burns
Ryan Burns
02:00 Apr-01-2008
Re: API-510 Pressure vessels inspection frequency
See excerpt below. I would perform UT thickness to determine corrosion rate and establish appropriate frequency in accordance with applicable jurisdictional authority. If T/A timing allows, it would likely be advisable to conduct internal insp on inlet and any sour service vessels as a minimum in conjunction with a full corrosion survey of vessels and associated piping.

Good luck,

RB.

INTERNAL AND ON-STREAM INSPECTION
The period between internal or on-stream inspections shall
not exceed one half the estimated remaining life of the vessel
based on corrosion rate or 10 years, whichever is less. In
cases where the remaining safe operating life is estimated to
be less than 4 years, the inspection interval may be the full
remaining safe operating life up to a maximum of 2 years.

----------- Start Original Message -----------
: Hello,
: I am working on a Gas gathering platform offshore. We need to know the frequency of the pressel vessels inspection, internal visual...As per API510, what is the frequency of a vessel to be inspected which is 2 and half years old?Someone please advise.Is it once in 5 years?We have a shut down coming and planning has to be done.
------------ End Original Message ------------




 
 Reply 
 
John O'Brien
Consultant, -
Chevron ETC , USA, Joined Jan 2000, 281

John O'Brien

Consultant, -
Chevron ETC ,
USA,
Joined Jan 2000
281
05:31 Apr-11-2008
Re: API-510 Pressure vessels inspection frequency
There is no simple answer to this question and I recommend you study API closely. The first issue is whether there is any jursidictional rules that will override API 510. The law comes first. Then there are options within 510 as to whether you plan using Risk based Inspection or Time Based Maximum Intervals as shown in API 510.
The time based intervals in 510 state that you must do an inspection at time of installation and when the vessel changes service or ownership. An external inspection on an interval not exceeding 5 years. Internal inspections not exceeding half the remaining life or ten yeras. The internal may be replaced by an on-steam inspection if the criteria of Para 6.5.2.1 are met.

And of course an RBI program may increase or decrease these intervals depending upon the analysis.


 
 Reply 
 
Mr. Engineer
Mr. Engineer
01:50 Aug-28-2008
Re: API-510 Pressure vessels inspection frequency
In addition to API 510, if your vessel is in US waters note that US Code of Federal Regulations, 2007 “Shipping” 46 CFR Subpart 61.10-5 “Pressure vessels in service”
• basically for vessels with annual COI’s all pressure vessels listed on the COI shall be examined or tested every 5 years. This includes an external and internal examination however it does get specific on what is required by the external examination and I believe its up to the attending surveyor. If the vessel is equipped with a manhole or inspection port it must be opened and an internal examination also conducted. No hydrostatic test is required unless a defect is found that, in the marine inspectors opinion, may affect the safety of the pressure vessel.

Also note the class rules for which your vessel falls under but if its ABS then it will also require the same inspection on a 5 yr interval.


----------- Start Original Message -----------
: Hello,
: I am working on a Gas gathering platform offshore. We need to know the frequency of the pressel vessels inspection, internal visual...As per API 510, what is the frequency of a vessel to be inspected which is 2 and half years old?Someone please advise.Is it once in 5 years?We have a shut down coming and planning has to be done.
------------ End Original Message ------------




 
 Reply 
 

Product Spotlight

FAAST-PA! OEM Patented phased Array for high speed UT inspection

Multiangle, Multifocus, Multifrequency, Multibeam. Instead of stacking UT electronics and having m
...
any PA probes, FAAST-PA is able to transmit all delay laws within ONE single shot in Real time.
>

Conformable wedge transducer

The conformability is obtained with a flexible membrane filled with water between the transducer and
...
the inspected component. The coupling between the membrane and the component requires a small quantity of water or couplant. The conformable wedge combines the acoustic performance of immersion technique with good coupling and low attenuation.
>

Research and Application Development For NDT

Acuren’s Research and Application Development specializes in the development of advanced ultraso
...
nic inspection techniques and systems for challenging inspection applications, with an emphasis on practical solutions which are field deployable. Services include manual and automated ultrasonic inspection system development, inspection technique optimization using laboratory scale studies and ultrasonic modeling (CIVA, BeamTool), preparing technical justification for technique evaluation and qualification (Probability of Detection and sizing accuracy studies), inspection/calibration/analysis procedure preparation to support field deployment of custom techniques, and development of custom imaging algorithms to support challenging inspection applications.
>

32:128PR PAUT & 2-ch TOFD Flaw Detector: SyncScan 2

●32:128PR PAUT with optional 2-ch TOFD to maximize your efficiency ●Support PR mode for corrosi
...
on inspection ●Multiple solutions for welds & corrosion ●Faster scan speed (Approximately 3 meters/minute) ●Light weight: 4kg only including battery
>

Share...
We use technical and analytics cookies to ensure that we will give you the best experience of our website - More Info
Accept
top
this is debug window