C/S Boiler Tube Inspection

Does anyone know of the best way to inspect carbon steel boiler tubes for leaks? These are approximate sizes.
38.1mm OD
31.7mm ID

38.1mm OD
63.5mm ID

 
 Reply 
 
Roger Duwe
NDT Inspector, API-510, 570, 653
MISTRAS, USA, Joined Jan 2009, 148

Roger Duwe

NDT Inspector, API-510, 570, 653
MISTRAS,
USA,
Joined Jan 2009
148
15:24 Apr-20-2009
Re: C/S Boiler Tube Inspection
In Reply to Ed at 07:46 Apr-20-2009 (Opening).

Hydro test the tubes, prefferably at a pressure greater than the Relief Valve setting. I would go 1-1/4 times PRV setpoint.

Second best is IRIS spinning-head UT inspection. Very slow, thus brutally expensive for a full boiler inspex.

 
 Reply 
 
Dent
Consultant, NDE Manager NDELevel III/3
NDT Consultant, Canada, Joined Nov 1998, 252

Dent

Consultant, NDE Manager NDELevel III/3
NDT Consultant,
Canada,
Joined Nov 1998
252
15:52 Apr-20-2009
Re: C/S Boiler Tube Inspection
In Reply to Roger Duwe at 15:24 Apr-20-2009 .

For gross leaks you may try an air test at low pressure. Use acoustics to listen for leaks.

 
 Reply 
 
Simon
Simon
19:45 Apr-20-2009
Re: C/S Boiler Tube Inspection
In Reply to Ed at 07:46 Apr-20-2009 (Opening).

You can try any of the Ultrasonic Leak Detectors with Ultrasonic Tone Generators to check the leaks in the pipes.

Sonatest has Soundscan units. Check their website

Simon

 
 Reply 
 

Product Spotlight

Ultrasonic Testing Immersion Tanks with Unmatched Scanning Features

TecScan’s non-destructive testing Ultrasonic Immersion Tanks & scanners are designed for high pe
...
rformance and demanding NDT testing applications. Our Scan3D™ line of High Precision Immersion Tanks are specifically designed for automated ultrasonic testing of complex composites parts used in aerospace and industrial applications.
>

NEW Wheel Type Phased Array Probe

DOPPLER NEW Wheel Type Phased Array Probe, more stable, new tyre makes lesser acoustic attenuation
...
, much lighter makes easier to handle, more slim size, magnetic and mechanical encoder optional etc...more
>

GEKKO - Portable Phased Array Testing with TFM in Real-Time

The portable phased array testing system GEKKO provides 64 parallel test channels. On creating testi
...
ng parameters the operator is assisted by the CIVA software. Due to its modular set-up the GEKKO instrument is suitable for operators of all skill levels.
>

IntraPhase Athena Phased Array System

The Athena Phased Array system, manufactured by WesDyne NDE Products & Technology, consists of a pha
...
sed array acquisition system and PC running IntraSpect software. A PC is used to perform acquisition, analysis and storage of the data. System hardware is capable of operating up to four data sets with any combination of phased array or conventional UT probes. NOW AVAILABLE IN 64-64 CONFIGURATION.
>

Share...
We use technical and analytics cookies to ensure that we will give you the best experience of our website - More Info
Accept
top
this is debug window