where expertise comes together - since 1996 -

The Largest Open Access Portal of Nondestructive Testing (NDT)

Conference Proceedings, Articles, News, Exhibition, Forum, Network and more

where expertise comes together
- since 1996 -
1994 views
Technical Discussions
Kosmos Qwantum corp
NDT Inspector
Russia, Joined Jun 2001, 3

Kosmos Qwantum corp

NDT Inspector
Russia,
Joined Jun 2001
3
03:19 Jun-14-2001
Tank inspection

I would like to get information on equipment for tank inspection of the latest modification(I am interested in inspection of bottom and walls

Best regards Chairman of the Technical Committee
A.Petrov
WWW.UZK.RU


 
 Reply 
 
Art Leach
Sales
GE Inspection Technologies, USA, Joined Apr 2001, 12

Art Leach

Sales
GE Inspection Technologies,
USA,
Joined Apr 2001
12
07:58 Jun-14-2001
Re: Tank inspection
: I would like to get information on equipment for tank inspection of the latest modification(I am interested in inspection of bottom and walls
.
: Best regards Chairman of the Technical Committee
: A.Petrov
: WWW.UZK.RU
.
If you plan to perfrom Ultrasonic inspections, I suggest you look at the Krautkramer line of Digital Thickness Gauges and in particular the DMS 2 with TopCOAT technology for reading through costings. Krautkramer also offers software for the data recording instruments which allows you to document the results of thickness surveys in the field, transfer data to the computer and print reports.

Contact you local Krautkramer sales representative for additional details....They can be located from the web site directory.

Art.



 
 Reply 
 
Meindert Anderson
Director
Olympus, USA, Joined Dec 1999, 5

Meindert Anderson

Director
Olympus,
USA,
Joined Dec 1999
5
08:29 Jun-14-2001
Re: Tank inspection
You may also check out Panametrics' line of high-end thickness gages for corrosion applications. The 36DL PLUS (with A-Scan) has lots of practical features including Echo-to-Echo, B-Scan with waveform recall, and simultaneous viewing of both live A-Scan and B-Scan. More information, including representation in Russia, is available on the company's website.

Meindert Anderson

: : I would like to get information on equipment for tank inspection of the latest modification(I am interested in inspection of bottom and walls
: .
: : Best regards Chairman of the Technical Committee
: : A.Petrov
: : WWW.UZK.RU
: .
: If you plan to perfrom Ultrasonic inspections, I suggest you look at the Krautkramer line of Digital Thickness Gauges and in particular the DMS 2 with TopCOAT technology for reading through costings. Krautkramer also offers software for the data recording instruments which allows you to document the results of thickness surveys in the field, transfer data to the computer and print reports.
.
: Contact you local Krautkramer sales representative for additional details....They can be located from the web site directory.
.
: Art.
.



 
 Reply 
 
John O'Brien
Consultant, -
Chevron ETC , USA, Joined Jan 2000, 280

John O'Brien

Consultant, -
Chevron ETC ,
USA,
Joined Jan 2000
280
02:05 Jun-14-2001
Re: Tank inspection
You are asking a very large question which you need to split up into out of service and on-stream inspection.

You also need to differentiate between standard uninsulated atmospheric tanks, insulated low pressure tanks and non metallic tanks.

Carbon Steel Atmospheric Tanks make up the bulk of the industry and fall under codes such as API 650/653 and EEMUA 159.

In service you can get at shells and roofs to perform UT thickness surveys with a wide range of ultrasonic devices. To avoid scaffolding there is an array of UT and MFL shell crawlers to determine remaining wall.

To determine corrosion activity of tank floors in service you can use Acoustic Emission or In Service Tank Robots. Robots have some limitations and can be expensive.

Once you take a tank out of service you should be looking at some form of overall floor scanning such as MFL or SLOFEC. Statistical coupon cutting or spot ultrasonics is an ineffective method and poses substantial risks of missing problem areas.

This is just a flavour of what needs to be considered



 
 Reply 
 
Christoph Schnitger
Christoph Schnitger
05:10 Jun-17-2001
Re: Tank inspection
You can use the ultrasonic thickness gauge T-Scope III
from Stresstel in addition to the MFL Inspektion in case,
p.ex. you use the MFL Scanner from the company 3P Services
in Lingen.

You find there profile under : http://www.3p-services.com
if you look for new or used ultrasonic equipemnt, such
as T_Scope III from Stresstel ( new equipment ) or such
as Panametrics 26 DL Plus ( used equipment ) please contact
me directly under : schnitger@eure.de

Thanks
C.Schnitger


 
 Reply 
 
MFE Enterprises, Inc.
MFE Enterprises, Inc.
07:01 Jun-19-2001
Re: Tank inspection
MFE Enterprises, Inc. designs, manufactures and sell magnetic flux leakage equipment for the inspection of tank floors. This equipment is adapted to inspect shells in some instances. Please visit our web site at www.mfescan.com to obtain information concerning our products and our company. We will be happy to address any questions you may have via email.


 
 Reply 
 

Product Spotlight

New PHAsis module for longitudinal weld seam inspection

PHAsis® Phased Array manual ultrasonic spot weld inspection device is now ideally suited for test
...
ing of longitudinally welded seams (e.g. Arplas® seam, short line seams) with a length of 3 to 12 mm.
>

FMC/TFM

Next generation for Phased Array UT is here now with FMC/TFM! Have higher resolution imaging, impr
...
oved signal to noise ratio, characterize, size and analyze defects better with access to several wave mode views and save raw FMC data for higher quality analysis.  Some of the benefits are:
  • Beautiful Image! Easier to understand what you're looking at
  • Completely focused in entire image or volume
  • Much easier to define setups before inspection
  • Easier to decipher geometry echoes from real defects
  • Oriented defects (e.g. cracks) are imaged better
  • See image from different wave modes from one FMC inspection
  • FMC data can be reprocessed/analyzed without going back to the field
>

HARDNESS TESTER TKM-459CE combi

TKM-459CE combi applies 2 methods of hardness control: UCI and Leeb. It provides high-accuracy tes
...
ting of metals and alloys as well as items of different sizes and configurations, their hardened layers and galvanic coatings. Device represents results in HB, HRC, HV and others. Shock-, dust- and water-proof housing with intuitive software make this gauge easy to use in all working conditions.
>

YXLON Cougar EVO

Scalable small footprint X-ray inspection systems for assembly and laboratory applications. The
...
YXLON Cougar EVO series was designed to provide the "best-in- class" inspection solutions for SMT, semiconductor, and laboratory assembly applications, while maintaining a small system footprint for maximum convenience. With optimized software and hardware, these systems produce higher quality and more consistent results than other electronics inspection systems currently on the market.
>

Share...
We use technical and analytics cookies to ensure that we will give you the best experience of our website - More Info
Accept
top
this is debug window