Steel reinforcement

I would like to have some suggestions concerning any NDT method for the evaluation of the corrosion of the reinforcement bars of some concrete structures. Please take into account that, if needed, some portions of the concrete can be also demolished to expose directly the steel bars.
Thank you very much in advance and best wishes.
Massimo Luca Schinelli
(Schinelli Consulting)


 
 Reply 
 
Martin Schickert
R & D,
Institute for Materials Research and Testing, Germany, Joined Jan 2000, 18

Martin Schickert

R & D,
Institute for Materials Research and Testing,
Germany,
Joined Jan 2000
18
09:27 Jan-21-2002
Re: Steel reinforcement
: I would like to have some suggestions concerning any NDT method for the evaluation of the corrosion of the reinforcement bars of some concrete structures. Please take into account that, if needed, some portions of the concrete can be also demolished to expose directly the steel bars.
: Thank you very much in advance and best wishes.
: Massimo Luca Schinelli
: (Schinelli Consulting)
.

There is a method called electro-chemical potential measurement that allows a relatively quick survey be made for suspected corrosion areas. Only experienced persons should carry out such examinations since a number of parameters has influence on the results.

In Germany, e.g.

Baustoff- und Bodenprüfstelle Kassel
Mr. Dumat
Knorrstr. 32
D-34134 Kassel
Phone +49 (0561) 7286438

offers such analysis.

There are at least two standards on electro-chemical potential measurements:

1. Swiss standard:
Durchführung und Interpretation der Potentialmessung an Stahlbetonbauteilen.
Merkblatt 2006, Schweizerischer Ingenieur- und Architektenverein, Ausgabe 1993-02

2. U.S.-American standard:
Standard Test Method for Half-Cell Potentials of Uncoated Reinforcing Steel in Concrete.
ASTM, C876-91, 1991



 
 Reply 
 

Product Spotlight

Varex Imaging Large Field of View (FOV) Digital Detector Arrays (DDAs)

A larger FOV DDA can reduce the space and volume of the X-ray inspection system on the factory floor
...
, enable faster scanning times, better throughput and better resolution images at a lower dose. Customers can also save time and money. With these benefits in mind, Varex Imaging has designed a family of large FOV detectors (4343HE, XRD 1611, 4343DX-I, 4343CT) for our industrial imaging customers.
>

ISAFE3 Intrinsically Safe Sensor System

ISAFE3 intrinsically safe sensor system of Vallen Systeme is especially targeted at the petrochemica
...
l - as well as oil and gas transportation industry. The sensor system is designed for permanent monitoring or periodic inspection tasks. Sensors are available for different AE-frequency ranges optimized for corrosion and fatigue crack detection and other applications. The ISAFE 3 sensor system consists of an AE-sensor (model ISAS3) certified according to ATEX/IEC for installation in zone 0, gas group IIC, IP68, 20 to +60 °C, and a signal isolator (model SISO3) certified for installation in zone 2. An ISAS3 sensor can be mounted in atmosphere or submerged, e.g. in water or crude oil. It is supported by mounting tools for temporary (magnets) or permanent (welded) installation. ISAFE3 supports automatic sensor coupling test and can be used with any AE signal processor supporting 28V supply at 90 mA peak, e.g. Vallen Systeme ASIP-2/A.
>

HD-CR 35 NDT Computed Radiography System

Portable high-resolution CR scanner for all radiography applications - weld testing, profile images
...
and aerospace. No matter what type of radiographic testing you are performing, the unique TreFoc Technology of the HD-CR 35 NDT imaging plate scanner always guarantees the highest image quality.
>

Conformable wedge transducer

The conformability is obtained with a flexible membrane filled with water between the transducer and
...
the inspected component. The coupling between the membrane and the component requires a small quantity of water or couplant. The conformable wedge combines the acoustic performance of immersion technique with good coupling and low attenuation.
>

Share...
We use technical and analytics cookies to ensure that we will give you the best experience of our website - More Info
Accept
top
this is debug window