We have a query, recently in the boiler we had a tube repair (butt joint) done by welder, material CS, Dia 50mm. After RT was done we found porosity in the capping.

Upon grinding the location, the porosity was found and removed and re-welding done.

my question is, do we need to do RT for the repair again?, as per the ASME Sec 1 (for our case) it should be done, but my question is to the experts if they know of code case where this can be waived or any lenience as such?

our concern is that we do not have enough time (process demands!!)

 
 Reply 
 
Anmol Birring
Consultant,
Birring NDE Center, Inc., USA, Joined Aug 2011, 786

Anmol Birring

Consultant,
Birring NDE Center, Inc.,
USA,
Joined Aug 2011
786
20:56 Sep-08-2019
Re: Re-shooting failed welding joint
In Reply to MHR at 16:34 Sep-08-2019 (Opening).

No option. To accept, RT has to be redone on the repaired area.

 
 Reply 
 
MHR
,
Pakistan, Joined Sep 2019, 2

MHR

,
Pakistan,
Joined Sep 2019
2
08:50 Sep-09-2019
Re: Re-shooting failed welding joint
In Reply to Anmol Birring at 20:56 Sep-08-2019 .

Hi,

thanks for the response, can you share your experience on joint failures due to Porosity? as per my knowledge from reading various articles etc people have gone 3 to 4 times over the prescribed limits in ASME Sec 1 or B31.1 on critical piping without having any issue.

 
 Reply 
 
laurie
Australia, Joined Feb 2019, 36

laurie

Australia,
Joined Feb 2019
36
03:07 Sep-10-2019
Re: Re-shooting failed welding joint
In Reply to MHR at 08:50 Sep-09-2019 .

If you need to comply with ASME Sect 1 Volumetric examination of welded butt joints then you will have to radiograph the joint if the unacceptable imperfections were detected by radiography.
There are no alternatives in ASME Sect 1 PW-11.1.

If you don't have to comply with ASME Sect 1 then pick a difference code and in particular AS 4037 allows unacceptable imperfections to be assessed and approved in accordance with AS/NZS 3788, such assessment taking into consideration stress levels, weld joint and material properties and operating environment.
You will need an engineer familiar with these standards who is approved to carry out this analysis in your location and the analysis might take days and the result could be that the imperfections are still unacceptable so it is a risky alternative.

 
 Reply 
 

Product Spotlight

NEW! The PragmaPro Instrument Platform

The PragmaPro is based on a modular cartridge technology and supports various NDT instrument modal
...
ities such as UT, PAUT, ECT and many more. This new platform is based on a machined, powder-coated aluminum frame for shock-proofness, best sealing qualities and maximum heat dissipation. This is practical to extend the outdoor temperature range and/or to extend the power injected in the transducers. The PragmaPro is aiming at a very wide range of applications, such as weld scanning, corrosion mapping and composite testing.
>

Sci Aps Z-Series Portable Handheld Analysers

The world’s only handheld analyzer that measures carbon content in stainless (yes even L-grades),s
...
teels, and cast irons. Also accepted for low Si analysis for sulfidic corrosion analysis, and is widely used in the power industry for Cr analysis, for flow accelerated corrosion applications.
>

HD-CR 35 NDT Computed Radiography System

Portable high-resolution CR scanner for all radiography applications - weld testing, profile images
...
and aerospace. No matter what type of radiographic testing you are performing, the unique TreFoc Technology of the HD-CR 35 NDT imaging plate scanner always guarantees the highest image quality.
>

ISAFE3 Intrinsically Safe Sensor System

ISAFE3 intrinsically safe sensor system of Vallen Systeme is especially targeted at the petrochemica
...
l - as well as oil and gas transportation industry. The sensor system is designed for permanent monitoring or periodic inspection tasks. Sensors are available for different AE-frequency ranges optimized for corrosion and fatigue crack detection and other applications. The ISAFE 3 sensor system consists of an AE-sensor (model ISAS3) certified according to ATEX/IEC for installation in zone 0, gas group IIC, IP68, 20 to +60 °C, and a signal isolator (model SISO3) certified for installation in zone 2. An ISAS3 sensor can be mounted in atmosphere or submerged, e.g. in water or crude oil. It is supported by mounting tools for temporary (magnets) or permanent (welded) installation. ISAFE3 supports automatic sensor coupling test and can be used with any AE signal processor supporting 28V supply at 90 mA peak, e.g. Vallen Systeme ASIP-2/A.
>

Share...
We use technical and analytics cookies to ensure that we will give you the best experience of our website - More Info
Accept
top
this is debug window