04:31 Jun-26-2006
Inspection of concrete pillars

Can any one knows that how to found deterioration in the concrete pillar which supports steam turbine foundations.

for any queries please contact

regards



    
 
 
Herman J. Quakkelsteijn
Herman J. Quakkelsteijn
07:36 Jun-26-2006
Re: Inspection of concrete pillars
RTD developed a pulsed eddy current technique able to detect general wall loss on ferrous objects without the removal of concrete. Technique is proven on the legs of spherical tanks with up to 200 mm of concrete.

----------- Start Original Message -----------
: Can any one knows that how to found deterioration in the concrete pillar which supports steam turbine foundations.
: for any queries please contact
: regards
------------ End Original Message ------------




    
 
 
John O'Brien
Consultant, -
Chevron ETC , USA, Joined Jan 2000, 278

John O'Brien

Consultant, -
Chevron ETC ,
USA,
Joined Jan 2000
278
01:26 Jun-27-2006
Re: Inspection of concrete pillars
You may need to provide more detail about the problem to solicit a response. i.e what thickness of concrete and damage mechanism you are seeking. If the concrete pillars are simple reinforced concrete, techniques such as Impact Echo or Acoutsic Emission from Corroding Rebar may be effective. Thicker sections and foundations techniques such as Ground Penetrating radar might provide data.



    
 
 
Ernst Niederleithinger
Ernst Niederleithinger
03:42 Jun-27-2006
Re: Inspection of concrete pillars
Dear Azhel Jamir,
There are a lot of possibilities: Ultrasonics, radar, x-ray, Schmidt-hammer,....
More information (geometry, accessibility,...) is needed to select proper method.
Regards, Ernst Niederleithinger
----------- Start Original Message -----------
: Can any one knows that how to found deterioration in the concrete pillar which supports steam turbine foundations.
: for any queries please contact
: regards
------------ End Original Message ------------




    
 
 
R. O. Duesing
R. O. Duesing
03:47 Jun-27-2006
Re: Inspection of concrete pillars
----------- Start Original Message -----------
: You may need to provide more detail about the problem to solicit a response. i.e what thickness of concrete and damage mechanism you are seeking. If the concrete pillars are simple reinforced concrete, techniques such as Impact Echo or Acoutsic Emission from Corroding Rebar may be effective. Thicker sections and foundations techniques such as Ground Penetrating radar might provide data.
------------ End Original Message ------------

Acoustic Emission is an excellent method for testing composite structures, in this instance concrete reinforced columns. On pre and post stressed concrete bridges and concrete support columns; i.e. highway overpasses, stepped loading and dynamic loading is applied while being monitored with Acoustic Emission sensors. The best scenario is to monitor suspect columns/spans at the same time with known good columns/spans in a comparative test.



    
 
 

Product Spotlight

MUSE Mobile Ultrasonic Equipment

The MUSE, a portable ultrasonic imaging system, was developed for in-field inspections of light-weig
...
ht structures. The MUSE consists of a motor-driven manipulator, a water circulation system for the acoustic coupling and a portable ultrasonic flaw detector (USPC 3010). The MUSE provides images of internal defects (A-, B-,C- and D-scan).
>

Spot weld inspection with Phased Array – PHAsis.one

The first PAUT spot weld inspection device offering a physical resolution of the spot weld diamete
...
r better than 0.35mm. Precise: more than 700 real UT measurements per spot weld. Easy to go: minimal training required due to the user friendly inspection software. Be sure: safe evaluation due to the imaging result display and automated creation of an evaluation proposal for the spot weld quality.
>

Lyft™: Pulsed Eddy Current Reinvented

PEC Reinvented—CUI Programs Redefined Corrosion under insulation (CUI) is possibly the greatest u
...
nresolved asset integrity problem in the industry. Current methods for measuring wall thickness with liftoff, without removing insulation, all have severe limitations. Eddyfi introduces Lyft — a reinvented, high-performance pulsed eddy current (PEC) solution. The patent- pending system features a state-of-the-art portable instrument, real- time C-scan imaging, fast data acquisition with grid-mapping and dynamic scanning modes, and flexibility with long cables. It can also scan through thick metal and insulation, as well as aluminum, stainless steel, and galvanized steel weather jackets. Who else but Eddyfi to reinvent an eddy current technique and redefine CUI programs. Got Lyft?
>

Alpha Pro Digital Radiography System

The Alpha Pro digital X-ray system is the ideal system for your NDT \r\nneeds, as it offers amazin
...
g 16 bit images which enable the highest \r\nlevel of detection and identification of hairline cracks. While weighing only 3kg (6.6lbs), this panel has the largest imaging area: 35 X 43 cm (14X17 in).
>

Share...
We use technical and analytics cookies to ensure that we will give you the best experience of our website - More Info
Accept
top
this is debug window
s